removedacct3
Allowing Ads
then it is 120V, but that seems highly unlikely.
Despite the fact it says "110V" eh?
The type plate says it is a HOGGLANSPRESS (Type 5 Volt 110 Watt 300), ELEKTRO-INDUSTRI FALKOPING SWEDEN.
Oops, a typo. A nasty one. The machine's type plate says 220 V instead of 110 V.
NOT !!then to wire a 110v in a 220v both hot, just use one leg and a ground.
NOT !!
first, this statement is confusing neutral and ground (protective); at best this would work in a three-phase AC distribution, with 220V between any two phases, and 127 (not 110) volts between any phase and neutral, and assumes that the neutral is made available at wall plugs (no reason to be if the installation has been converted to 220V).
second, and most important: no amateurish improvisation with AC mains
Check to see the voltage on the metal plate. It is probably the standard two pronged 220-240V. If it starts smoking or gets too hot on 220-240V, then it is 120V, but that seems highly unlikely.
Despite the fact it says "110V" eh?
I missed that. Then a step down transformer or down converter is in the future.
That is what I missed in the original post.
Oops, a typo. A nasty one. The machine's type plate says 220 V instead of 110 V.
the italian cord was wired to the right pin and the center pin. the left pin was blank. so it was wired to one live phase and the center ground... there is no neutral. ... our neutral and ground both tie in to an earth ground at the entrance box generally hard wired to a cold water pipe.