From the numbers you give, you would have a maximum of five changes of air per hour - Possibly not the best ratio for a darkroom. Axia suggest a minimum of ten changes per hour, so you might want to consider a bigger fan.
If you just had a fan running in the darkroom that pulls filtered (HEPA) air in, and you had a small vent to the outside some distance from this, this would give you positive pressure. Instead of sucking the air in, you would be pushing it out. Seems like a more effective way to vent it.
Also, if you used citric acid for stop bath, and an odorless fixer (see link below) most of your problems would be solved. I would still use positive pressure venting though.
http://www.freestylephoto.biz/6200-Arista-Premium-Odorless-Liquid-Fixer-32-oz.
It's not just the cfm of the fan, but also the characteristics of the exhaust vent. The type of venting (smooth or pleated), diameter, length, and number of bends. So, as an example, you used 4" pleated venting and have 3 90 deg bends, you've substantially reduced the airflow going out.
As to placement of fan and inlet, you've got that right.
Also think about where your air is coming in.
If you've got an outlet fan in one corner and the rest of the room is well sealed, how's the air going to come in to replace what's being taken out? Under the door, around windows cracks etc, or it just doesn't and the fan does nothing.
If you do have an inlet vent, and it's on the same wall as the outlet, you're not going to get much bad-air out either, it'll just replace that side of the room unless you've got a ceiling fan or something mixing the air up.
Best practice is to put an inlet vent (or fan) down low, and an outlet fan (or vent) up high diagonally opposite each other, such that your biggest source of bad-air (like fixer in a tray) is pretty much on a straight-line between those two.
Check to see that air is actually flowing through the inlet, and out the exhaust.
can you tell me the math of how you figured that out?
My darkroom is 11x11' with 7' ceilings (basement).[...] I put a bathroom exhaust fan (70cfm) above