Hey Everyone,
I'm working on my second darkroom and need to make a better ventilation system as I will be doing the RA4 process.
My down stairs bathroom is 54"x106"x81" = 269 Cubic Feet
The exhaust fan I'm interested in does 205 CFM.
If I did the calculations right, that's 45.7 room changes of air per hour.
From my research tonight, it is recommended to have changes of 10-15 per hour.
So I think I'm okay for exhaust.
1. Now my question is did I do the math right?
2. Can I use this louver for the air input? Or can someone recommend a louver that has a fan for positive pressure?
https://www.bhphotovideo.com/c/prod...1212_L_1212_Light_Tight_Darkroom.html/reviews
Thanks for reading this.
And thanks for any advice shared
Be well
Best Regards,
Kevin